Hi all,  I am installing Bosch  NTC dual pressure 261 230 340 sensors  to a Link G4+ Fury. I will be wiring 4 of these sensors  to AN Temp 1-4 for temp inputs.

As I understand AN Temp 1-2 come with internal pull up resistors. However, Aux temp 3-4 doesnt. 

My question; install all 4 Bosch temp sensors correctly, I will need to install external 1k ohm pull up resistors for AN Temp 3-4 for all temp sensors to read accurately. Is this correct?

I scan thru the forums and online help docs but cant seem to confirm this. 

Link to comment
Share on other sites

An Temp 1,2,3 & 4 all have internal pullup resistors, The difference between An Temp 1&2 vs 3&4 is that 1&2 are configurable so they can be 1kOhm, 10kOhm or no pullup

So no you don't have to add any external pullup resistors to use An Temp 1,2,3&4 with standard NTC temperature sensors. The pressure sensors will need to be wired to An Volt inputs